Investigating Extreme Oscillations in Low-Inertia Generators within IEEE 39-Bus System with Heterogeneous Inertia Constants #594
Barbara258
started this conversation in
General
Replies: 2 comments 1 reply
-
|
For a system with generators of low inertia, you will expect to see large rate of change of frequency at these generators. This is not numerical instability - the result appears stable. It's possibly just due to the fact that some generator inertia is low.
You can gradually increase them to see the smooth out of the curves, or you can do an eigenvalue analysis of the steady-state system, which should show the same oscillation frequency that is observed.
… On Mar 25, 2025, at 2:38 AM, Barbara258 ***@***.***> wrote:
<x-msg://8/url>Dear Hantao Cui,
I've encountered an interesting phenomenon while simulating load disturbances in the IEEE 39-bus system with different generator inertia settings. I'm seeking your insights on the following behavior:
When generators have significantly different inertia constants (M values), and I apply a sudden load increase disturbance to the system, I observe extreme oscillations in both rotor speed and COI frequency specifically for the low-inertia generators (as shown in Figures 1 ). The oscillations appear highly erratic and significantly differ from the expected frequency response pattern.
However, when I set the generator inertia constants to be more homogeneous (with smaller differences between units), these extreme oscillations disappear, and all generators show more consistent frequency responses (as shown in Figures 2).
My specific settings in the heterogeneous case were:
COI 1: M values of 25-30 (ultra-high inertia)
COI 2: M values of 10-12 (medium inertia)
COI 3: M values of 3-4 (low inertia)
COI 4: M values of 2 or lower (extremely low inertia)
While in the homogeneous case, all generators had M values between 6-15.
What causes these extreme oscillations specifically in low-inertia areas under heterogeneous conditions? Is this related to numerical instability in the simulation, or does it represent actual physical phenomena we might observe in real power systems with high penetration of inverter-based resources?
Any insights on the underlying mechanisms and potential mitigation strategies would be greatly appreciated.
Thank you
1.png (view on web) <https://github.com/user-attachments/assets/d0f66b34-69da-47c7-b058-eddfca409b72>
2.png (view on web) <https://github.com/user-attachments/assets/33b2f60c-83d5-4ff7-98aa-e4a73ca20fbe>
—
Reply to this email directly, view it on GitHub <#594>, or unsubscribe <https://github.com/notifications/unsubscribe-auth/ABSNZA6QVKK3F6GXWXBOO3D2WD2UXAVCNFSM6AAAAABZWXZF66VHI2DSMVQWIX3LMV43ERDJONRXK43TNFXW4OZYGEZDKNZWHA>.
You are receiving this because you are subscribed to this thread.
|
Beta Was this translation helpful? Give feedback.
1 reply
-
|
You can do a small-signal stability analysis on the heterogeneous inertia case and see the oscillation modes. The result is somewhat expected because if you imagine a spring network with both heavy and light springs, the light springs will oscillate faster and may oscillate against each other, while the heavier ones will respond slower. |
Beta Was this translation helpful? Give feedback.
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment



Uh oh!
There was an error while loading. Please reload this page.
-
Dear Hantao Cui,
I've encountered an interesting phenomenon while simulating load disturbances in the IEEE 39-bus system with different generator inertia settings. I'm seeking your insights on the following behavior:
When generators have significantly different inertia constants (M values), and I apply a sudden load increase disturbance to the system, I observe extreme oscillations in both rotor speed and COI frequency specifically for the low-inertia generators (as shown in Figures 1 ). The oscillations appear highly erratic and significantly differ from the expected frequency response pattern.
However, when I set the generator inertia constants to be more homogeneous (with smaller differences between units), these extreme oscillations disappear, and all generators show more consistent frequency responses (as shown in Figures 2).
My specific settings in the heterogeneous case were:
While in the homogeneous case, all generators had M values between 6-15.
What causes these extreme oscillations specifically in low-inertia areas under heterogeneous conditions? Is this related to numerical instability in the simulation, or does it represent actual physical phenomena we might observe in real power systems with high penetration of inverter-based resources?
Any insights on the underlying mechanisms and potential mitigation strategies would be greatly appreciated.
Thank you
Beta Was this translation helpful? Give feedback.
All reactions